Phase-shifted carrier PWM for cascaded H-bridge on C2000 + RTBox HIL
Hi everyone,
I am conducting HIL experiments using a C2000 LaunchPad and an RTBox, with a single-phase cascaded H-bridge inverter. Since the cascaded H-bridge uses phase-shifted carrier PWM modulation, I tried configuring the PWM module in the TI C2000 target accordingly, but it doesn’t seem to achieve the desired result.
The demo examples I found only show a single H-bridge, and there is no demo for phase-shifted modulation.
Attached is my simulation.
Does anyone know how to achieve cascaded H-bridge control in this setup? Any advice would be greatly appreciated.
3H_c2000_openloop.plecs (78.6 KB)
Your overall approach works fine but there are a few details that will cause your model to not work in hardware implementation.
  1. The 28379D has certain restrictions on how PWMs can be synchronized. See Figure 15-7 from the 2837xD Technical Reference Manual. PWM’s must be synchronized in groups of 3. In your original model you were trying to synchronize ePWM3 via a synchronization input, which it does not have. Only ePWM1, ePWM4, ePWM7, etc. have these synchronization inputs. I modified your model to have the synchronization chain set appropriately. One note is that there is a 2 ePWM clock delay between synchronized groups. You can correct for that by having a “dummy” PWM trigger the other two PWMs that will connect to your outputs. However, in that case you still are restricted by the IO capabilities of this target hardware and would have to do a bit more work to remap the RT Box inputs.
  2. You have resistors in series with your voltage sources which is not allowed for the sub-cycle average switch models. The DC port must be across an ideal voltage source or capacitor.
  3. The effective switching frequency is 60 kHz and you are using an RT Box 1 with a 5 usec step size. This is only 3.3 model steps per period on the RT Box, so the real-time performance will be poor. The results are much better with the FlexArray solver of the RT Box 2/3/4 as the step size is 147 nsec vs. 5 usec on the CPU in your model. However, you can use a purely resistive load for your testing purposes where the results are better.
Here is the modified model: 3H_c2000_openloop_BL.plecs
Hi Bryan Lieblick,
I see your solution and the explanation – this really solves my current problem and clears up some doubts I’ve had. Your method is super helpful! I’ll study your ideas carefully, as I’m sure they’ll be very useful to me.
Thanks again for your response, and have a great day!